164

A new generation of engineers has realized they can push heat pumps to the limit.

you are viewing a single comment's thread
view the rest of the comments
[-] LengAwaits@lemmy.world 2 points 4 months ago* (last edited 4 months ago)

At the time of writing, real-time data suggests that for every kilowatt-hour of electricity Ritchie’s heat pump consumes, it delivers 5.5 kilowatt-hours of heat—a coefficient of performance, or COP, of 5.5.

[-] LodeMike@lemmy.today 0 points 4 months ago

You can easily almost double that if you're willing to break the pump in a few years.

But usually that's more expensive per BTU/other heat unit because the pumps are expensive. That's why I asked.

[-] evranch@lemmy.ca 4 points 4 months ago

Double would be a COP of over 10. That's a stretch for an overbuilt GSHP and not even slightly feasible for air-air.

High COPs are usually easy on a compressor as they represent low compression ratios and low differential temps. For example I can hit around COP 7 in cooling on my scrap heap GSHP, with an evap temp around 10C and condenser temp around 20C. That's a high side pressure around 100 psi and only 30 psi of differential, "barely working" as far as the compressor is concerned.

The only way I know to get high COPs is to have an oversized condenser and a way to get your refrigerant below ambient, like evaporative, ground source or overnight radiant so you can get the compression ratio down, unless you know a secret in which case I'm not afraid to burn out a compressor or two trying it out!

[-] LodeMike@lemmy.today 1 points 4 months ago

I don't rember the details of how it works. I think it just reduces the torque or something? Maybe it doesn't work on newer pumps or they already do it.

[-] evranch@lemmy.ca 4 points 4 months ago

Oh I think I know what you're talking about, abusing a minisplit by idling the inverter back too far. Effectively you have a hugely oversized condenser for the tiny flow, under the right conditions like a cool night you can get ridiculous subcooling.

But COP is irrelevant in this case because you've derated the actual BTU to near zero, you aren't moving any refrigerant.

Also yes this will kill your compressor because the minimum speed is set where it will get enough oil flow. Run it too slow, and it won't pick up oil and eventually seize up. You also could end up running the suction in vacuum which is also hard on compressors.

[-] LodeMike@lemmy.today 2 points 4 months ago* (last edited 4 months ago)

Thats it thank you.

this post was submitted on 03 Jul 2024
164 points (97.1% liked)

Climate - truthful information about climate, related activism and politics.

5186 readers
533 users here now

Discussion of climate, how it is changing, activism around that, the politics, and the energy systems change we need in order to stabilize things.

As a starting point, the burning of fossil fuels, and to a lesser extent deforestation and release of methane are responsible for the warming in recent decades: Graph of temperature as observed with significant warming, and simulated without added greenhouse gases and other anthropogentic changes, which shows no significant warming

How much each change to the atmosphere has warmed the world: IPCC AR6 Figure 2 - Thee bar charts: first chart: how much each gas has warmed the world.  About 1C of total warming.  Second chart:  about 1.5C of total warming from well-mixed greenhouse gases, offset by 0.4C of cooling from aerosols and negligible influence from changes to solar output, volcanoes, and internal variability.  Third chart: about 1.25C of warming from CO2, 0.5C from methane, and a bunch more in small quantities from other gases.  About 0.5C of cooling with large error bars from SO2.

Recommended actions to cut greenhouse gas emissions in the near future:

Anti-science, inactivism, and unsupported conspiracy theories are not ok here.

founded 1 year ago
MODERATORS